Lone working on isolated and dead HV equipment

Spurt 17:58 - 9.7.2015 av Stephen Robertson|Siste svar 5:59 - 13.7.2015 av Hans Olav Arnesen

Stephen Robertson

What are the rules when working on isolated and proven - dead HV equipement? EG Transformer inspection with feeder breaker racked out and locked? Is it acceptable to work alone after isolation and grounding?

Helpful answer marked by forum leaderLøst
FSE Lav- og høyspenning

Godkjent FSE-opplæring for deg som jobber med elektriske anlegg. Hold deg oppdatert slik at du og dine kolleger får en trygg arbeidsdag. Les mer.

Svar (1)

Hans Olav Arnesen

Postet 5:59 - 13.7.2015

§ 12 in FSE describes:

During all work on or in the vicinity of a high voltage installation there must be at least twopersons present in order to be prepared for coping with an accident situation.

The guidance to § 12 describes:

The two-person requirement may be waived if the risk assessment indicates that thiswould not contribute to any increased risk for the worker concerned. This could, forexample apply to work on a cable installation where temporary earthing is installed atthe ends of the cable by means of an enclosed switching setup, capacitive voltage testingand a fixed earthing system.

Watch: http://www.dsb.no/Global/Publikasjoner/2013/Andre/safety_regulations_related_to_the_maintenance_and_operation_of_electrical_installations.pdf

Legg til svaret ditt

Trainor logo

Registrer deg og bidra til Norges største fagforum for sikkerhet.
Allerede medlem? Logg inn

Registrer deg nå
Trainor logo
Opplæring for fagfolk. Av fagfolk.

Registrer deg og bidra til Norges største fagforum for sikkerhet.

Registrer deg

Allerede medlem? Logg inn

Relevante kurs

Trenger du sertifisering, opplæring eller kurs i elsikkerhet? Enten du velger e-læring, et webinar eller et instruktørledet kurs fra Trainor, er kurset laget av våre fremste eksperter. Alt til det beste for din læring og sikkerhet.